Hi All,
Facing an issue with the UPS not being able to provide power backup on mains failure during gaming sessions. While gaming, as soon as the power fails, the UPS shuts down almost immediately and emits a constant beep (which indicates Online Overload Fault according to the UPS manual),
On the other hand if the system is idle during a power failure, the UPS signals low battery warning almost immediately.
This is a 2200VA APC UPS which should be able to handle up to 1200W according to the specifications.
I don't believe that the system should reach that kind of power even under load.
However, I am not sure if the GPU transient power spikes are causing any issues here, or if there is any other issue.
I had bought this UPS about 8 months ago, and just need it to power the PC long enough to be able to safely shutdown.
Here's my configuration:
CPU: Ryzen 5 5600x
Ram: 32 GB DDR4
Motherboard: MSI B450M Pro-Vdh Max
GPU: Galax RTX 3080 Ti 12GB
PSU: Corsair RM1000e 1000W
UPS: APC Easy UPS 2200VA Line Interactive (BVX2200LI-IN)
Any help will be much appreciated.
N
NegruSama
04-15-2021, 12:29 PM #1

Hi All,
Facing an issue with the UPS not being able to provide power backup on mains failure during gaming sessions. While gaming, as soon as the power fails, the UPS shuts down almost immediately and emits a constant beep (which indicates Online Overload Fault according to the UPS manual),
On the other hand if the system is idle during a power failure, the UPS signals low battery warning almost immediately.
This is a 2200VA APC UPS which should be able to handle up to 1200W according to the specifications.
I don't believe that the system should reach that kind of power even under load.
However, I am not sure if the GPU transient power spikes are causing any issues here, or if there is any other issue.
I had bought this UPS about 8 months ago, and just need it to power the PC long enough to be able to safely shutdown.
Here's my configuration:
CPU: Ryzen 5 5600x
Ram: 32 GB DDR4
Motherboard: MSI B450M Pro-Vdh Max
GPU: Galax RTX 3080 Ti 12GB
PSU: Corsair RM1000e 1000W
UPS: APC Easy UPS 2200VA Line Interactive (BVX2200LI-IN)
Any help will be much appreciated.

R
Raqet
Member
222
04-15-2021, 01:46 PM
#2
You can't rely on no-load voltage for any conclusions. They lack failed cells, yet their performance might still be reduced. Consider swapping the batteries, as recommended...
R
Raqet
04-15-2021, 01:46 PM #2

You can't rely on no-load voltage for any conclusions. They lack failed cells, yet their performance might still be reduced. Consider swapping the batteries, as recommended...

T
Thekidcool
Junior Member
22
04-15-2021, 02:59 PM
#3
Examining this page shows the specifications and usage details. At 1200W, it provides 22 seconds of backup. The UPS is likely outdated, as batteries typically last 3 to 5 years under normal conditions. If you experience frequent power interruptions, the battery life may be insufficient. Given the quick drain during light loads, a replacement is probably necessary.
T
Thekidcool
04-15-2021, 02:59 PM #3

Examining this page shows the specifications and usage details. At 1200W, it provides 22 seconds of backup. The UPS is likely outdated, as batteries typically last 3 to 5 years under normal conditions. If you experience frequent power interruptions, the battery life may be insufficient. Given the quick drain during light loads, a replacement is probably necessary.

A
AssasinBot1
Junior Member
21
04-15-2021, 04:46 PM
#4
It appears your battery or UPS might be faulty.
A
AssasinBot1
04-15-2021, 04:46 PM #4

It appears your battery or UPS might be faulty.

M
MaddyForce18
Member
93
04-19-2021, 10:45 AM
#5
During gaming your device is drawing close to 40Amps from a battery close to a 4-5C load. Because of its compact size and likely poor maintenance, it probably has degraded significantly and hasn't received proper charging, which is typical for cheaper electronics. The voltage dropped below the inverter's cutoff point instantly. You'll need a much larger SLA with accurate frequent charging using suitable voltages and longer high-voltage periods. I purchased an expensive marine-grade charger from professionals that even fails to meet these requirements.
M
MaddyForce18
04-19-2021, 10:45 AM #5

During gaming your device is drawing close to 40Amps from a battery close to a 4-5C load. Because of its compact size and likely poor maintenance, it probably has degraded significantly and hasn't received proper charging, which is typical for cheaper electronics. The voltage dropped below the inverter's cutoff point instantly. You'll need a much larger SLA with accurate frequent charging using suitable voltages and longer high-voltage periods. I purchased an expensive marine-grade charger from professionals that even fails to meet these requirements.

T
timmieboy200
Member
53
05-02-2021, 12:30 AM
#6
Even when operating at maximum capacity, the highest load power should remain under 1000W for the setup, indicating roughly a minute of backup time. The UPS is relatively new, purchased around eight months ago. I began noticing this problem only recently.
T
timmieboy200
05-02-2021, 12:30 AM #6

Even when operating at maximum capacity, the highest load power should remain under 1000W for the setup, indicating roughly a minute of backup time. The UPS is relatively new, purchased around eight months ago. I began noticing this problem only recently.

A
alevy3131
Member
156
05-03-2021, 09:21 AM
#7
Hi, thank you for your patience. Based on this, I suggest considering a higher battery capacity UPS or exploring a different type of battery and UPS altogether.
A
alevy3131
05-03-2021, 09:21 AM #7

Hi, thank you for your patience. Based on this, I suggest considering a higher battery capacity UPS or exploring a different type of battery and UPS altogether.

D
Dam1yo
Member
145
05-03-2021, 05:48 PM
#8
It seems the battery might be faulty. Check if your UPS displays the battery voltage or if you have a multimeter for testing. Also, confirm whether the battery has a specified voltage rating.
D
Dam1yo
05-03-2021, 05:48 PM #8

It seems the battery might be faulty. Check if your UPS displays the battery voltage or if you have a multimeter for testing. Also, confirm whether the battery has a specified voltage rating.

K
kwbabe
Junior Member
4
05-05-2021, 12:24 AM
#9
The voltage isn't visible, but I'll need to inspect the UPS. I'm uncertain about the battery voltage rating, so I'll look it up on the APC page.
K
kwbabe
05-05-2021, 12:24 AM #9

The voltage isn't visible, but I'll need to inspect the UPS. I'm uncertain about the battery voltage rating, so I'll look it up on the APC page.

M
mumustrak
Senior Member
729
05-06-2021, 06:37 PM
#10
It looks like pulling 40 amps makes sense.
Calculating it another way: 40 times 12 volts equals 480 watts.
Or, using a battery feeding inverter at 40 amps, it would be 40 times 12 volts, also giving 480 watts.
If the backup batteries are in a 24-volt package, 20 amps times 24 volts also results in 480 watts.
This is the power the inverter draws when you lose electricity and the battery has to support your computer.
M
mumustrak
05-06-2021, 06:37 PM #10

It looks like pulling 40 amps makes sense.
Calculating it another way: 40 times 12 volts equals 480 watts.
Or, using a battery feeding inverter at 40 amps, it would be 40 times 12 volts, also giving 480 watts.
If the backup batteries are in a 24-volt package, 20 amps times 24 volts also results in 480 watts.
This is the power the inverter draws when you lose electricity and the battery has to support your computer.